Yes, obviously not included at night as per a manual part set but... how does it decide the difference between that and a full set exit route stray / straggler?
Does it wait until a door is opened before announcing activity in a part-set omitted zone?
As you can see Part B of building regs asks for grade B but from an out dated document. It should be BS 5839-6:2013
BS 5839-6:2013 supersedes BS 5839-6:2004, which is withdrawn.
Landing zone isn't included in part/night set. The dimension and flex have this too. No use if you have someone who works on nightshift and you have to part set and leave while they are in bed.
Hi Michael
Your house requires a system designed and installed to Grade A LD2 which is a full fire alarm system.
Your electricians are right not to get involved in something that will not conform to building regulations.
You should have been made aware of this at the design stage along with costs.
Its not fit for purpose,
analogue addressable fire alarm system, if you've a half decent architect or project manager you'll should have already been advised of this
Get another electrician to sign off or do the interlinked bit
Total blag , what's reason they won't sign off an Interlinked system ? They only signing of electrical part , all down ra , where's doc cubit
the sound bombs require remote power
The prem is not a proper fire panel
If you want 'proper' fire then use proper fire kit. DO NOT use intruder gear in a fire alarm
For simplicity of setting i like euro mini/46 programmed for intelligent set. Swip the tag and go to bed, system realises you haven't opened a final exit and automatically part sets. If you leave via a final exit system automatically full sets. Pensioners love it.
shame they did away with that functionality on the app versions.
Jim, if you are reading why did they take that feature out? Customers love it.