Premier 48 Digicom Outputs For Fire Detection


martlewis

Recommended Posts

Posted

I'm trying to get a digicom programmable output to go 0v when a fire zone is activated or fire on keypad is pressed. I'm using wintex to program.

So far I have output 1 programmed as areaD (which the fire zones are assigned to), and set as option 11 fire. The voltage doesn't change on the output when fire is activated. Have tried changing to PA and when I press PA on the keypad the output goes 0v, but as soon as I go back to fire on that output nothing happens. Anyone got this working?

Posted

Doesn't matter guys, sorted it. Had to enable "unarmed fire comms" in Area options otherwise the output only triggers when system/area is armed.

Archived

This topic is now archived and is closed to further replies.