jonnyg2k5 Posted January 2, 2009 Posted January 2, 2009 i'm just adding an m12 smoke heat detector to my unconfigured eurosec cpx panel. my problem is that one of the config options on the m12 is 'latching reset' or 'auto reset' but which option is compatable with the cpx? thanks for reading!!
Monty Posted January 3, 2009 Posted January 3, 2009 We don't use the cpx panels but do use the M12 smoke det If the M12 is on its own zone you can just set the detector to auto reset if it is sharing a zone you would want it to latch and use an output to drop the 12 supply (detector reset ) www.AllanMoncrieffAlarms.com