Posted

Does the relay work if you put a straight neg and pos on it from the Aux supply? If so, how is it connected and how are you testing the output?

Trade Member

Posted

Does the relay work if you put a straight neg and pos on it from the Aux supply? If so, how is it connected and how are you testing the output?

Thamks for reply, I can get the led to go on and off with the test toggle on the keypad and the relay clicks but still get a closed circuit on my meter.

Posted

How are you wiring the relay trigger?

Posted

Thamks for reply, I can get the led to go on and off with the test toggle on the keypad and the relay clicks but still get a closed circuit on my meter.

I have the pos strait from the 12v and the neg from o/p 1 on the smart rio. then a pair in c & n/c

Posted

Have you metered out the voltage from the Aux 12vdc and the output when triggered?

Also the other side of your n-nc is that clean, could be a short on there.

Posted

Have you metered out the voltage from the Aux 12vdc and the output when triggered?

Also the other side of your n-nc is that clean, could be a short on there.

Normally open stays open all the time too. there are 2 realays and both are the same either they are both shot or more likely wired wrong. dont really know where to go with it maybe I am missing something?

Posted

You have to check the voltage is changing when testing the output.

What relays are they? As you say are they correctly wired?