Posted

You have to check the voltage is changing when testing the output.

What relays are they? As you say are they correctly wired?

Just small pcb mounted mini relay. Will check the output voltage how should they be wired? Thought I was right but starting to consider Mcdonalds as a career;q

Posted

First thing is to check the voltages are switching.

Test the relays on a battery, supply voltage to the coil. Which would be the single pair at the back, the DPDT at the front in a bank of 6.

Should be fairly straight forward.

Posted

First thing is to check the voltages are switching.

Test the relays on a battery, supply voltage to the coil. Which would be the single pair at the back, the DPDT at the front in a bank of 6.

Should be fairly straight forward.

Thank you all very much! I will post to let you know how I got on>

Posted

Please do its always good to hear the outcome.

Posted

Normally open stays open all the time too. there are 2 realays and both are the same either they are both shot or more likely wired wrong. dont really know where to go with it maybe I am missing something?

Could be voltage ok, but output unable to supply/sink enough current for relay to fully operate.

Posted

Best thing is to post a pic of them wired in then we can pass comment on them being wired right. But from what you have said they are. Not latching relays or something daft are they?

Found the problem I had the o/p polarity set to neg instead of pos. really appreciate all your efforts guys!