As James, new battery at that age. If that does not clear the fault then you can try the monitor hardware, think its a local setting, not sure its in a wintex menu.

Posted

No of course, but I assume the OP is not brain dead.

Not brain dead, but I was assuming the OP has no idea tho.

I wouldn't check a battery with the built-in voltage readings.

You are correct about the "Monitor Hardware Shuffle", had to do this a couple of times.

Posted

I have fitted the new battery yesterday, logged in via Wintex and it looks like everything is back to normal. No more Alerts on the screen either.

 

Thanks for all your help and advice guys.

Graham

twitter: ithorizon1

http://www.ithorizon.co.uk

  • 2 years later...
Posted

Ive got a fault on a Premier 24. I put a new battery in 3 months ago after a battery fault and the customer has called me back as its appeared again.

Investigation shows that the battery is only holding 7v but then checking the charging voltage its only 6.7v.

I have 13.2 v on the Aux and bell outputs but the battery leads are only pumping 6.7v down them.

Keypad diagnosis confirms this when reading system status. Without any adjustable pot on the PCB or blown fuse, how can I adjust the charging voltage back to 12v ??

A nearly retired previous installer !

Posted

did it have a knackered battery in the past?

Yes, i think the previous battery whilst fairly new got totally drained in a long duration power cut.

A nearly retired previous installer !

Posted

New install in 2011, had 3 batteries since but think it had a long outage around 2013. Last fitted a batt in March, another one today.

I'll verify with Tex Tech support tomorrow as customer is a neighbour so a bit awkward to quote £100 for a new PCB even though outage wasnt my fault !

Thanks for the quick responses.

A nearly retired previous installer !

Posted

Might be worth checking the battery charging current, nominally 500mA or thereabouts. Also a current limiting resistor gone high value, look for burn marks around resistors in that area.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.