hundleton1 Posted October 15, 2014 Posted October 15, 2014 Hi all I'm new here, i have worked in the industry for years but never did to much with honeywell alarms, i was a cctv installer for 11 years, mostly stuck to AV and CCTV, i have a Honeywell Accenta allarm to install on my parents house next week, all looks straight forward apart from iv read the manual and the 3 programs are confusing me slightly, i understand program 1 is everything, then program 2 Timed states it should be entry route and P3 will delay if an entry route is triggered first but if not will go off instantly. my question is i take it P1 uses P2 zones for entry/exit delay as i could not see how to specify specific zones as entry/exit? also I'm looking a setting up one program that just protects the Garage via a PIR, its gong to have 4 PIR's 1 Kitchen (this will be entry/exit point) 1 x Hall 1 x Back room 1 x Garage My Plan was P1 everything P2 Kitchen PIR P3 Garage PIR on its own. hopefully this would allow P3 to protect the garage only ? thanks in advance for any help
james.wilson Posted October 15, 2014 Posted October 15, 2014 Id put door contacts on your entry doors. But yes you can enable / disable the circuits in each of the programmed sets, ie p1-3 Also id put a dt in the garage not a pir securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount.
hundleton1 Posted October 15, 2014 Author Posted October 15, 2014 is it p2 that defines te entry zones ?
9651 Posted October 15, 2014 Posted October 15, 2014 All points can do different things in the different programmes. For P3, make all zones unused bar the garage, enable the setting option to either timed or instant. Job done.
hundleton1 Posted October 15, 2014 Author Posted October 15, 2014 sorry got it now manual was not clear
Recommended Posts
Archived
This topic is now archived and is closed to further replies.