gfarrel Posted December 18, 2014 Posted December 18, 2014 Hello I have installed an Optima control panel with one PIR, one door contact and a bell box for my garage. The panel has been setup with 2 zones (a door contact on zone 1 and a PIR in zone 2). I am able to set\unset the alarm, however, if I hide in the garage whilst someone else sets the alarm and they leave via the entry/exit door (zone 1) and then I move and get picked up by the sensor, the alarm does not trigger, but instead it triggers the entry timer (I expected the alarm to trigger in this scenario). When I set\unset the alarm at the control panel keypad and then exit\enter via the garage door, I am picked up by the PIR, so the sensor is part of my entry\exit route. I have setup program 1 as follows - zone 1 = used\timed zone 2 = used\inhibited zones 3 to 8 - unused I have been scratching my head on this one…an any help on this would be much appreciated. GF Quote
secureiam Posted December 18, 2014 Posted December 18, 2014 If the pir is picking you up, then its programed wrong if the entry starts and not going into alarm. Quote
gfarrel Posted December 18, 2014 Author Posted December 18, 2014 Hi thank for your reply. How do I program the panel to ignore the pir when I set\unset the panel but also trigger the alarm if the door contact is not opened? thanks Quote
gfarrel Posted December 18, 2014 Author Posted December 18, 2014 The pir is programmed as inhibited but the alarm does not trigger as per my original post. Quote
9651 Posted December 18, 2014 Posted December 18, 2014 Well it cant be. Door as entry exit. PIR as inhibited. Thats what that zones does. Inhibits when the entry time starts, immediate when it hasn't seen an entry timer start Time to re check ;-) Quote
gfarrel Posted December 19, 2014 Author Posted December 19, 2014 9651 - thanks for your 2nd post, I agree with you and hence the reason for the head scratching. I will re-check program setup tonight. thanks Quote
efficient_systems Posted December 19, 2014 Posted December 19, 2014 This panel has 3 programmes, each programme carries a zone type map, make sure the zone type is set correctly for all programmes you are using. Quote
al-yeti Posted December 19, 2014 Posted December 19, 2014 This panel has 3 programmes, each programme carries a zone type map, make sure the zone type is set correctly for all programmes you are using. Yeah many setup like that, they want more money to setup part set aswell Quote
gfarrel Posted December 20, 2014 Author Posted December 20, 2014 Evening Double-checked my program 1 setup and it's as I described in my OP - zone 1 = used\timed zone 2 = used\inhibited zones 3 to 8 - unused I performed a factory reset and reprogrammed, just to start from scratch again. efficient_systems - Looking at the Engineer's manual, the zone setup is the same for all 3 programs, the only thing that I have changed on program 1 is to set zones 3-8 as unused and left programs 2 and 3 unchanged, is this okay? Is there any else that can cause the pir to activate the entry timer when the entry route has not been activated? Could I have a duff panel......? GF Quote