I have a G2-20 panel with RF and a 8 rio added using 3 groups, 1 house 2-3 out buildings. I have noticed a few times if 1u 2s 3s and there is a mains fail groups 2-3 unset. Need to double check what happens when all are set and mains fail. The panel reports mains fail on G2-20 and P Rio. But why is the system unsetting the other 2 groups when mains fails both units have good batteries?

Link to comment
Share on other sites

Yes the system runs fine on battery, there are two one in main panel and another in powered rio, batteries check out ok and I don't get any battery faults on panel.

 

I seem to remember the RF G3 had too be assigned to a zone for groups, main panel was full these are all house sensors ie G1, the P-RIO is for an outbuilding G2 but not all 8 were used so assigned it to a un used zone on there, but not sure why his would cause the mains fail to unset.

Link to comment
Share on other sites

12v incoming to a smart Rio can cause all sorts of issues. To be honest though I've seen it done many a time and no problems whatsoever. In fact, I'm guilty, when we first started using them I did it on my first smart Rio.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.



×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.