jkno Posted June 28, 2015 Posted June 28, 2015 (edited) I've finally gotten round to putting the recessed door contact (Knight A51MULTI G2) for the entry/exit rather than using the hallway PIR. I wired everything up and re-enabled zone 1 but it was displaying tamper. So I stripped back the contact and tested all the resistances 2.2 secure, 6.9 active, 1/0 tamper. I also checked the resistances at the alarm box to make sure I didn't have a break in the cable. To confirm I linked the contact circuit into Zone 6 which was spare and wintex diagnostics registers 2.2 secure (healthy). Finally to confirm Zone 1 I bridged and programmed zone 1 to always closed which returned an active state (unhealthy) Does it sound like Zone 1 is dead and I need to replace the board or could it be a common faults that can be rectified without a board replacement? Edited June 28, 2015 by jkno Quote
james.wilson Posted June 28, 2015 Posted June 28, 2015 If you move the door to another circuit does it work correctly or is it in tamper too Quote securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount.
jkno Posted June 28, 2015 Author Posted June 28, 2015 I moved the circuit to zone 6 and it works fine. Quote
james.wilson Posted June 28, 2015 Posted June 28, 2015 Zone 1 is setup to the correct eol values etc Quote securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount.
jkno Posted June 28, 2015 Author Posted June 28, 2015 Yep it's sent to Double Pole/EOL like all the other active zones. It doesn't seem to register the bridge I've put in whether it's open or closed. I've stuck the multi meter across zone (no circuit wired up) and it registers as an open/broken circuit. Quote
charlie6 Posted June 28, 2015 Posted June 28, 2015 Probably done this already but, Have you removed all wiring from zone 1 terminals and linked them with the correct eol's ? Quote
jkno Posted June 28, 2015 Author Posted June 28, 2015 I didn't wire a resistor over over the terminals but did confirm the circuit was the correct resistance with the multimeter. I also wired a bridge over and switched it to an always closed circuit which it was registering as open (active). I've emailed texecom I expect it's an replacement board job. Quote
al-yeti Posted June 28, 2015 Posted June 28, 2015 So what happens if you select it as eol and bridge with eol as abovd Quote
charlie6 Posted June 28, 2015 Posted June 28, 2015 So zone 1 is conventional then, and the remaining zones are fsl, is that correct ? Sorry Al-yeti, typed over you, my mistake. Quote
jkno Posted June 28, 2015 Author Posted June 28, 2015 Just to remove any confusion all zones are FSL the contact circuit I want on zone 1 registers at 2.2 secure 6.9 active. As part of my investigation after ruling out any fault at the contact or circuit I remove the circuit from the zone, bridged and reprogrammed as always closed. The zone isn't registering the bridge and thinks its open/active. I'll try a 2.2 resistor just to confirm but think it will be futile because the contact circuit was confirmed with the multimeter at 2.2 and a basic bridge on always closed isn't registered meaning something isn't right on the zone. Quote