Shembo Posted April 29, 2016 Author Share Posted April 29, 2016 I did think that al-yeti. It's about a 50m run but it's hidden along the backs of fencing, under a driveway, across a roof, you know the sort of thing. I did swap to two spare cores in the cable in case one of the others were damaged, (did this on my first visit) but to no avail. I've ordered a new Rio now. I'll swap that out and see what happens. In the mean time, I'll still entertain any fresh ideas that anyone comes up with. Thanks for all your help everyone, I'll let you know what happens. Quote Link to comment Share on other sites More sharing options...
james.wilson Posted April 29, 2016 Share Posted April 29, 2016 Id be drawn towards a cable problem to be honest. What sort of cable is it? Quote securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment Share on other sites More sharing options...
Shembo Posted April 29, 2016 Author Share Posted April 29, 2016 I'm pretty sure it's 6 core cca james.wilson. In what way do you think it might be a cable problem mate? Quote Link to comment Share on other sites More sharing options...
GalaxyGuy Posted April 29, 2016 Share Posted April 29, 2016 Yes, from the description of the cable installation, it would probably make sense to perform some tests on the cores for water ingress Etc. The RIO's are very reliable. A cable swinging along the back of a fence - less so. Quote Link to comment Share on other sites More sharing options...
Shembo Posted April 29, 2016 Author Share Posted April 29, 2016 Haha, I make you right on that Galaxyguy. How would I go about testing it? I've 'belled it out' and put my meter on it and it's coming back at under 1k ohm. Does that sound about right for the distance? Quote Link to comment Share on other sites More sharing options...
al-yeti Posted April 29, 2016 Share Posted April 29, 2016 Just replace the cable don't worry about taking old one out and either get external grade, armoured or pipe it Quote Link to comment Share on other sites More sharing options...
Shembo Posted April 29, 2016 Author Share Posted April 29, 2016 Yeah I guess you're right al-yeti. That's going to take some planning though so I think I'll swap the Rio as soon as it comes and hope that solves it. If not I'll do the cable. Thanks again guys. Quote Link to comment Share on other sites More sharing options...
james.wilson Posted April 29, 2016 Share Posted April 29, 2016 1k would be about 1000m on copper cable. 1k is too high imo Quote securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment Share on other sites More sharing options...
Nova-Security Posted April 29, 2016 Share Posted April 29, 2016 (edited) 2 hours ago, Shembo said: Haha, I make you right on that Galaxyguy. How would I go about testing it? I've 'belled it out' and put my meter on it and it's coming back at under 1k ohm. Does that sound about right for the distance? 56 minutes ago, james.wilson said: 1k would be about 1000m on copper cable. 1k is too high imo But is the above with the 680ohm EOL resistor in place Or a 1k instead of the 680 ? Edited April 29, 2016 by Nova-Security Quote www.nova-security.co.uk www.nsiapproved.co.uk No PMs please unless i know you or you are using this board with your proper name. Link to comment Share on other sites More sharing options...
james.wilson Posted April 29, 2016 Share Posted April 29, 2016 I assumed by 'belled' it was shorted to read. Quote securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount. Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.