Theres also every chance it could be a faulty base or bad connetion drawing too much current.

I would also do a reset point threshold comp. any time you change a device

Every day is a school day

Posted
15 hours ago, Taco said:

You wont get high ident faults on mcp's mate, i wouldnt even bother looking there. 

It certainly looks like the air quality is being affected and this is whats triggering the faults.

Could you change the type of detectors to co or heats? That would resolve the issue, other than that, some sort of barrier at the door or extractor fan

seems like the air quality. Anyway, seems like its impossible to change the type of head from smoke to any other type unless I reprogrammed the eprom inside as per maker's advice. And, as a crew here, we are not allowed to do changes on it.

11 hours ago, goncall said:

if you've changed ion to hpo you will have to change  programming in consys or you will get id  faults, also any faulty device on the loop can cause low and high id faults on other devices, a faulty mcp causing id faults is common only way to prove is to discon one device at a time and link the loop thru and check the levels unless you have a shorting device which speeds up the process its  a pain of a fault to trace 

Thanks mate,I got your point, but, when the technician came here 6mos ago (this problem not yet exist), he adviced us that HPO (MR901T) is ok to replace ion (mF901)without problem, because ion is not available in the market. Only optical (MR901) needs reprogramming. With regards to mcp, can you please elaborate more how to prove it?

 

10 hours ago, Taco said:

Theres also every chance it could be a faulty base or bad connetion drawing too much current.

I would also do a reset point threshold comp. any time you change a device

Mate, what do you mean by a reset threshold comp?

Posted

The system basically adjusts the range in sensitivity of a detector due to dirt/age to reduce false alarms, so after a period of time that threshold will rise to compensate for a 'dirty' chamber.

When you replace a head that value is obviously way higher as the new detector is cleaner.

Defaulting the threshold is telling the panel your detector is clean

 

I think its under 3.9 something in the menu. Best bet is to download a manual for it if you dont have one

Every day is a school day

Posted
On 1/14/2017 at 7:11 PM, Taco said:

The system basically adjusts the range in sensitivity of a detector due to dirt/age to reduce false alarms, so after a period of time that threshold will rise to compensate for a 'dirty' chamber.

When you replace a head that value is obviously way higher as the new detector is cleaner.

Defaulting the threshold is telling the panel your detector is clean

 

I think its under 3.9 something in the menu. Best bet is to download a manual for it if you dont have one

Yep, seems like that's the best option. Is there any link you can provide? Because I'm still struggling at our internet connection here.
Anyway, I was wondering what is the proper voltage for each loop? As I check, it has 16volts max in each loop (A,B,C,D loops), but what I know in each head, min voltage should be 18volts and 32volts at max... Any comment for this?

Posted

Are you checking the voltage across the terminals with the loop connected? 

You should be getting 24v output across all 4 loops with nothing connected.

If you are getting 16v with nothing connected then this is way too low and you're looking at a faulty main board.

The detectors will work within certain ranges, but your panel will start registering all sorts of weird and wonderful issues if its only outputting 16v. 

If you're getting 24v with nothing connected you're going to have to start splitting the loop and measuring the voltage at the detectors until you find where the drop is, and that will be your fault.

 

Ive attached a pdf that should explain quite a few things for you too

 

Minerva Addressable Service Instructions.pdf

Every day is a school day

  • 1 month later...
Posted

All instances of this I've come across are contaminated heads, sometimes they clean up and clear but quite often come back into fault and need replacement

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.