xpertalarms Posted November 1, 2017 Author Posted November 1, 2017 Nova- groups are disabled, offending zone isn't on soak Al- sorry mate, I wasn't being very clear...I wasn't near a keypad so connected up to the panel and used RSS with the virtual keypad, no luck so tried a physical keypad Quote
GalaxyGuy Posted November 1, 2017 Posted November 1, 2017 So, two possibilities? It's either a faulty PCB, or some (corrupt) setting that you're re-loading in with RSS after defaulting. I would try loading the config on a test panel and ensuring that it's not something being held in the config before going through the hassle of replacing the panel PCB. May be worth having a look at the RSS roll-back points and checking the diffs. If you want to duplicate the site in RSS, then change the PIN's to default and send the mdb file to me, I can load onto a test panel here in my office and quickly check it for you if you want. I have all Dimension variants plumbed in and sitting on test at the moment. Quote
xpertalarms Posted November 6, 2017 Author Posted November 6, 2017 Thanks for the offer GalaxyGuy, I have tried it on our demo board 48 and it appears to be fine. I've also been back to site and defaulted the panel, tried setting from a default and it's still showing. Looks like it's time to change the panel. Quote
GalaxyGuy Posted November 6, 2017 Posted November 6, 2017 I've not seen a zone fault auto omit without also indicating the fault with the zone and asking for confirmation. Assuming that the resistances showing on the panel bang on 1k/2k when you press the hash key. It's a strange one. Quote
xpertalarms Posted November 6, 2017 Author Posted November 6, 2017 Us neither, will keep you updated! Quote
Nova-Security Posted November 6, 2017 Posted November 6, 2017 (edited) 1 hour ago, GalaxyGuy said: I've not seen a zone fault auto omit without also indicating the fault with the zone and asking for confirmation. Assuming that the resistances showing on the panel bang on 1k/2k when you press the hash key. It's a strange one. Version 5.20 G3-48 did do forced omits on open or faults without any confirmation, took a while for honeywell to believe us Edited November 6, 2017 by Nova-Security Quote www.nova-security.co.uk www.nsiapproved.co.uk No PMs please unless i know you or you are using this board with your proper name.
SouthernBrad Posted November 8, 2017 Posted November 8, 2017 Sounds daft but have you let the system set with the circuit omitted, Then unset it? Quote
norman Posted November 8, 2017 Posted November 8, 2017 On 11/6/2017 at 19:24, Nova-Security said: Version 5.20 G3-48 did do forced omits on open or faults without any confirmation, took a while for honeywell to believe us Had this first on an ATM room, I'd replaced the controls and it was on a shunt lock, by the time the lock was thrown it omitted both DT's in the room. You could hold the door open and it would set on the lock, omitting the door too iirc. Quote Nothing is foolproof to a sufficiently talented fool.
Nova-Security Posted November 8, 2017 Posted November 8, 2017 Had it where a RIO had been damaged and the system had Call Alarm Co on the keypad but would still set with RIo missing and override the remote reset, Galaxy tech came to site as they didn't believe it. Firmware updated all fine. Quote www.nova-security.co.uk www.nsiapproved.co.uk No PMs please unless i know you or you are using this board with your proper name.