Posted

Hi

got a problem with a Scantronic 9751 it won’t see the zones on a hard wired 8 Zone expander board it will see the expander tamper switch but none of the zones.

 

indicated  fully supervised loop with link is there somewhere in the programming that you have to do but the last one I did I just put FSL link in and it could see zones 9 onwards. 

I can program the zones from 9 onwards but it won’t see them when I walk test.

 

any help would he great.

Posted

Andddd.... here he is.

 

So... I am guessing you've done a cold restart following fitting?

 

I am guessing you've wired the FSL zones as per the instructions?

 

And I'm guessing it is addressed as 'Expander 1'?

 

I had a funny situation with a 9853 a few years back where you had to use Address 2 due to the on-board zones (if using FSL). I wasn't expecting it, I still though '1' would be an acceptable address...

 

9954.thumb.PNG.08826838c2b2eeec99bee973d2aaf90d.PNG

So, I've decided to take my work back underground.... to stop it falling into the wrong hands

 

Posted
1 hour ago, datadiffusion said:

Andddd.... here he is.

 

So... I am guessing you've done a cold restart following fitting?

 

I am guessing you've wired the FSL zones as per the instructions?

 

And I'm guessing it is addressed as 'Expander 1'?

 

I had a funny situation with a 9853 a few years back where you had to use Address 2 due to the on-board zones (if using FSL). I wasn't expecting it, I still though '1' would be an acceptable address...

 

9954.thumb.PNG.08826838c2b2eeec99bee973d2aaf90d.PNG

Reminds me of a 9571 that would accept a wired expander until I removed the wireless expander , probably what your saying , I just got rid of the wireless was easier to wire everything up lol

 

One day that ricochet will catch up

Posted

Yes zones are correctly wired with 4k7 with 2K2 end EOL.

I have addressed 

Address 1:keypad

address 2 :expander

address 3 keypad

 

so can you have a keypad adressed as 1 and and expander adressed as 1 

thanks 

 

Posted (edited)

Keypad and expander addresses are mutually exclusive... It isn't like Menvier M / x5 kit.

 

I expect the system may be assuming that as there is an expander 2, there is also an expander one somewhere and hence offering up zone 9 onwards... Though it shouldn't. You may only have to enter zone 17 to 24 and it should work.

 

But personally I'd change jumper back to 1, keypads to 1 and 2, cold restart, hopefully you won't need to default...

Edited by datadiffusion

So, I've decided to take my work back underground.... to stop it falling into the wrong hands

 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.