Low res showing on zones tested voltage on pirs zones appears correct 0.872v zone number 1003 1008 1013

replaced resistors eol 1k ,when system is unset it appears 3 faults low res nothing else system arms without problem called monitoring company they said unaware of faults the system was installed by myself as a foreigner for a pals pub ??? 

 

 

Posted

What's the resistance with respect to 0v on the zone wire with the zone wire removed from the panel screw terminal?  With the zone wire removed from the terminal does it show any voltage (DC or AC) on the wire when measured against 0v?

 

Next step is to swap zones and see if the problem remains or follows the wired devices. If it remains, replace the PCB. If it follows the wiring, then further investigation of the sensors and wiring is required.

 

The Dimension firmware was changed at some point to only log marginal low/high res to the engineer log, so not surprising that these are not being reported to the arc.

  • Upvote 1
Posted
31 minutes ago, grandmaster14 said:

hello galaxy guy yes I checked the resistance 836 ohms checked zone 2 with respect to 0v and that reads 996 ohms 

thanks 

So it's ok then?

Posted
36 minutes ago, al-yeti said:

So it's ok then?

no change from what I said the strangest thing is I checked the zone in the engineer menu and when the pir activates the zone goes from low res to closed 

back to low res all the zones that are normal show open when PIR activates think it might be best to replace pcb 

 

Posted

Are you saying that zone 1002 is ok, or that you swapped the zones over ?

 

The values are out of range. Ie. 836 Ohms is too low.  Moisture in the cabling / sensor, wrong resistors, additional resistors Etc ?  You need to fault find the reason for 836 ohms on a 1k/2k circuit.   When the detector is activated, it's opening the contact bringing the circuit into the 900 to 1200 ohms range and not 2k. 

 

Are you sure the detector doesn't have integral resistors and you're adding more in parallel ?

 

Zone closed needs to be between 900 to 1.2k ohms (best 1k).  Open between 1.3k and 3.5k ohm (best 2k).

Posted
On 29/01/2018 at 00:34, grandmaster14 said:

Going directly to panel zones 1pir each zone at the panel 

Model no and pictures of detector?

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.