mr_g_99 Posted May 25, 2018 Posted May 25, 2018 I'm adding a PC5208 Low Current Output Module Expander to my PC1832 Panel for the purpose of triggering an auto-dialer's inputs. My smokes are programed as 07 - 'Delayed 24 Hour Fire' . I'd like to program one of the outputs on the PC5208 to activate when a only a fire alarm occurs - that's easy by assigning PGM option 10 'Latched System Event' and further defining that event as "Fire Event Only' BUT I'd like the output not to activate until the 30 second communication delay (as defined in the Delayed 24 Hour Fire assignment) or the lack of acknowledgement (*72) has elapsed. Any ideas very welcome. Thanks Quote
al-yeti Posted May 25, 2018 Posted May 25, 2018 19 minutes ago, mr_g_99 said: I'm adding a PC5208 Low Current Output Module Expander to my PC1832 Panel for the purpose of triggering an auto-dialer's inputs. My smokes are programed as 07 - 'Delayed 24 Hour Fire' . I'd like to program one of the outputs on the PC5208 to activate when a only a fire alarm occurs - that's easy by assigning PGM option 10 'Latched System Event' and further defining that event as "Fire Event Only' BUT I'd like the output not to activate until the 30 second communication delay (as defined in the Delayed 24 Hour Fire assignment) or the lack of acknowledgement (*72) has elapsed. Any ideas very welcome. Thanks Extra timer ? I assume there's no option to set a delay time? Quote