forumflyer Posted May 31, 2018 Posted May 31, 2018 Hi, I have a client wanting me to connect up a paxton net2 unit with a texecom alarm system as it should be able to unset and set the alarm on entry and exit. The problem i have is paxton diagram is not that clear. It says i need an momentary key switch input 2 wires this is coming off a relay (where do i wire these to on the texe?) And also from the alarm it want a voltage free status output again 2 wires, where do they go and what colours Seems very hard to find an answer on this considering paxton sell alot of these units! Thanks Quote
james.wilson Posted May 31, 2018 Posted May 31, 2018 the from alarm pair is an open close clean switch to show the paxton if its armed or not. the to pair will go to a zone programmed as keyswitch momentary Quote securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount.
forumflyer Posted May 31, 2018 Author Posted May 31, 2018 Thanks for your swift responce So the from alarm (texe unit) which two am i wiring it from on the texe board Quote
james.wilson Posted May 31, 2018 Posted May 31, 2018 from a relay that operates when the system is armed Quote securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount.
sixwheeledbeast Posted May 31, 2018 Posted May 31, 2018 Would require dedicated ACU to conform to BS8243, probably not applicable here but worth mentioning. Texe only have closed contacts on the 88 and up. Quote