Posted (edited)

Hi all, following a few garage break-ins on our estate lately, I decided to change to a Rio from a single zone so I can add a PIR.

 

Everything went ok, the system detects the Rio, Rio set to slave via link 4, but I can only get one zone to work.All are set to intruder.

 

zone 8 Roller shutter contact - works normally

zone 7, PIR -  Nothing

zone 6, Door contact, Nothing

 

I did have the Door Contact working on zone 2 at one time when I tested it before installing. It is set to address 3
 

I have searched online for guides on installing nd programming, but can find very little. Photo is from when I tested it.

 

Thanks for reading, Keith

 

58876573-8188-48C6-B05F-6A5C80061E74.thumb.jpeg.63cf190ec018da61dbed73042a97677b.jpeg

Edited by Keef
Posted
36 minutes ago, james.wilson said:

Why are you using it as a slave. That's for shunting etc

Lol I wondered why he was doing that 

Posted (edited)
8 hours ago, al-yeti said:

Lol I wondered why he was doing that 

By the sound of it I am doing it in error. I followed another post I found online. I have only cut one side so I can easily reattach it it.

Hopefully you lot can tell me the correct way to do it.

There are only 1k resistors in the unused zone terminals, plus 2x1k on the other 3 zones

 

Thanks, Keith 

Edited by Keef
Posted
32 minutes ago, james.wilson said:

The 1k restistors should be in the devices not at the rio

Sorry, not worded very clearly.

The resistors are at the 2 contacts and the PIR, only the unused zones have them at the Rio

Posted
9 hours ago, Nova-Security said:

 

Before anything remake link 4

Link 4 remade and still the same ?

Posted

Whats the panel you are using, RIO is addressed as 3 so the circuits would start at 1031

 

The wiring looks like its going to ciruit 1 and 2 on the rio but the leg of circuit 1 looks like there isnt anything in it on the picture.

 

In your first post you mention zones 6.7.8 but the EOL resistors are in 6,7,8 and where are you getting the power for the PIR from?

www.nova-security.co.uk

www.nsiapproved.co.uk

No PMs please unless i know you or you are using this board with your proper name.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.