al-yeti Posted August 12, 2023 Posted August 12, 2023 8 hours ago, MrHappy said: there's ya problem.... I'd assume the fuse on the I/O is unmonitored ? you checked it ?? Enforcer will power the master blaster? Quote
Bad-Yeti Posted August 12, 2023 Author Posted August 12, 2023 36 minutes ago, al-yeti said: Enforcer will power the master blaster? No, the Master Blaster is powered by a separate 240v feed the siren out is just the relay switch for the blaster. Hail be to the Yeti's Quote
james.wilson Posted August 13, 2023 Posted August 13, 2023 5 hours ago, Bad-Yeti said: Aye I guess. So are Pyronix alarms not exactly great? What are a good make? Anything apart from pyronix and risco Quote securitywarehouse Security Supplies from Security Warehouse Trade Members please contact us for your TSI vetted trade discount.
Bad-Yeti Posted August 13, 2023 Author Posted August 13, 2023 23 hours ago, MrHappy said: If as has been suggested, I disconnect the battery and do a I guess hard restart will it lose all its settings? Quote
MrHappy Posted August 13, 2023 Posted August 13, 2023 17 hours ago, Bad-Yeti said: So are Pyronix alarms not exactly great? Fitted correctly they are bullet proof. 1 hour ago, Bad-Yeti said: If as has been suggested, I disconnect the battery and do a I guess hard restart will it lose all its settings? If you wish to default use setting - "CLEAN START" from the engineering menu However, lets start with the very basics ? Loosen the 2 screen under the panels back plate so you can hang the front panel underneath. Is the ribbon from l/O pcd fitted correctly? Have you +12v & com on DC voltage with multi meter ? Remove the trigger for MB or EWD & touch it to com your device should sound? Yes = programming issue(s) No= fuse of wiring issues Quote Mr Veritas God
Bad-Yeti Posted August 13, 2023 Author Posted August 13, 2023 (edited) Ok I've discovered the problem there was a short and it had taken out one of the fuses after all is there any way to arm the system as I don't have any fuses and can't get any more until tomorrow. Is it possible to on the system with that fault? I note your comment Mr happy and you don't need to worry I shouldn't be doing any more alarms to be honest with you I didn't even want to do this one in the first place lol. Edited August 13, 2023 by Bad-Yeti Quote
Bad-Yeti Posted August 13, 2023 Author Posted August 13, 2023 Okay, when I tested the siren the output from the I/o is only 2.38 volts for this sound up and 1.85 for the stroke that's with both fuses replaced Quote
MrHappy Posted August 14, 2023 Posted August 14, 2023 On 13/08/2023 at 14:07, Bad-Yeti said: Okay, when I tested the siren the output from the I/o is only 2.38 volts for this sound up and 1.85 for the stroke that's with both fuses replaced between output & 12v ? Quote Mr Veritas God
Bad-Yeti Posted August 14, 2023 Author Posted August 14, 2023 Got it all sorted. Looks like all the advice I got from the supplier was wrong. That the Siren and Strobe are negative switches against the 12v not positive against the common, it damaged the I/O board. Quote
al-yeti Posted August 14, 2023 Posted August 14, 2023 54 minutes ago, Bad-Yeti said: Got it all sorted. Looks like all the advice I got from the supplier was wrong. That the Siren and Strobe are negative switches against the 12v not positive against the common, it damaged the I/O board. Manual would have been better to use Board is cheap and available Quote