al-yeti Posted September 18 Posted September 18 4 hours ago, john123 said: The other detectors have a short non resisted wire joining alarm and tamper (B and D). Do I need to do this in the P15 to complete the loop with 4 core? Thanks. John. As above don't bother Quote
john123 Posted September 24 Author Posted September 24 The comments have been really helpful. Thanks. Now I understand the Scantronic 9448+ does not use EOL resistors. The replacement Texecom Capture P15 PIR has an adjustable internal resistor for EOL. How do I take this out of the circuit? Do I just set to O/C O/C.? Many thanks again. Quote
ian.cant Posted September 24 Posted September 24 7 hours ago, john123 said: Do I just set to O/C O/C.? Many thanks again. Yes Quote
john123 Posted October 2 Author Posted October 2 Great. Worked well. The manual says 97 Enter for walk test and OMIT to leave but there is no OMIT on this keypad (scantronic 9448+). Do I use 99 Enter, or other? Many thanks. Quote
PeterJames Posted October 2 Posted October 2 1 hour ago, john123 said: Great. Worked well. The manual says 97 Enter for walk test and OMIT to leave but there is no OMIT on this keypad (scantronic 9448+). Do I use 99 Enter, or other? Many thanks. I think the enter button will take you out of walk test, 99 enter takes you out of engineering Quote