JPW Posted Monday at 17:04 Posted Monday at 17:04 (edited) Really strange one... it's been a while since I installed a Texecom unit (and that was Veritas) but I've just installed a new Premier Elite 24 (wired) panel. All zones are working, and I can set the system, but when the system alarms (when I fail to enter the user code on entry) but external bell siren does not sound. The strobe on the bell box does however, as does the internal keypad sounder of course. When I test the Bell from the Engineer Utils on the keypad, both the bell and the strobe work respectively. When you remove the lid, the bell siren also sounds as it should for tamper. What could cause the bell siren to not activate when the system goes in to alarm? All wiring must be correct if the Bell test works surely? As its a brand new install, there isn't some default setting I need to set to enable the bell siren is there? (can't imagine why) Bell wiring: Panel wiring: Thanks Edited Monday at 17:10 by JPW Quote
MrHappy Posted Monday at 17:28 Posted Monday at 17:28 does the bell delay state 0 mins is the bell in the same area (AB) as the zones ? Quote Mr Veritas God
JPW Posted Monday at 17:40 Author Posted Monday at 17:40 (edited) I haven't programmed anything to change the defaults, is it set to these by default? Will take a look. Edited Monday at 17:40 by JPW Quote
al-yeti Posted Monday at 17:45 Posted Monday at 17:45 5 minutes ago, JPW said: I haven't programmed anything to change the defaults, is it set to these by default? *** take a look.*** does the bell delay state 0 mins is the bell in the same area (AB) as the zones ? Quote
ian.cant Posted Monday at 22:03 Posted Monday at 22:03 Has the system actually completed the setting function? Set the system and trigger a device without starting the entry timer. Quote
JPW Posted Monday at 22:12 Author Posted Monday at 22:12 7 minutes ago, ian.cant said: Has the system actually completed the setting function? Set the system and trigger a device without starting the entry timer. Same problem. Regardless of how the alarm is triggered (either entry timer expiring or just immediately walking in front of a PIR that is set to Guard) the bell doesn't sound but the internal keypad and strobe goes off... Quote
al-yeti Posted Monday at 22:56 Posted Monday at 22:56 43 minutes ago, JPW said: Same problem. Regardless of how the alarm is triggered (either entry timer expiring or just immediately walking in front of a PIR that is set to Guard) the bell doesn't sound but the internal keypad and strobe goes off... Does bell work if you open cover Does bell work if you remove tamper at panel? Does strobe flash if bell doesn't activate? Quote
JPW Posted Monday at 22:58 Author Posted Monday at 22:58 (edited) 2 minutes ago, al-yeti said: Does bell work if you open cover Does bell work if you remove tamper at panel? Does strobe flash if bell doesn't activate? The bell doesn't go off if I open the panel cover Bell doesn't go off if tamper is removed at panel Bell DOES go off if I open the bell box cover Strobe only flashes on alarm being activated/triggered Edited Monday at 22:58 by JPW Quote
al-yeti Posted Monday at 23:02 Posted Monday at 23:02 3 minutes ago, JPW said: The bell doesn't go off if I open the panel cover Bell doesn't go off if tamper is removed at panel Bell DOES go off if I open the bell box cover Strobe only flashes on alarm being activated/triggered You doing this now ? Lol And are these all the steps you done before I or others ask more Ps it's what I meant , bell cover not panel , but thanks for detailed response Quote
sixwheeledbeast Posted Tuesday at 01:14 Posted Tuesday at 01:14 What are the comfort LED's doing? Have you triggered it with a bell test or giving the trigger a negative. Quote