bellman Posted August 9, 2005 Posted August 9, 2005 No, don't fit one later Breff's advice is correct, fit one NOW before it starts annoying your neighbours with false alarms or possibly damages your control panel. Regards Bellman Service Engineer and all round nice bloke ) The views above are mine and NOT those of my employer.
gla.ssfp Posted August 9, 2005 Posted August 9, 2005 might be a good idea to fit the filter anyway, They are very good and not too dear anyway. I got called to an existing domestic a while back which was activating everytime the lights were switched on, Fitted filter and cured it straight away Best to avoid the situation in the first place but if cables installed it dont sound like you got much choice
gla.ssfp Posted August 9, 2005 Posted August 9, 2005 great minds think alike bellman You win on typing speed though
Deltaseven Posted August 9, 2005 Posted August 9, 2005 Seconded. Fit an ACT1313 - a magic piece of kit!
Mavrick_001 Posted August 9, 2005 Posted August 9, 2005 The site above, call act, "dave" is the main man there.... these things only have 3 wires 12v 0v and earth, scantronic aren't that bad with induced ac but it'd be worth fitting one as they're only a few quid compared to anoyed neighbours knocking at your door..... act131... the life saver!!! CCTV Intruder Access Control Tony Hughes, Proprietor, TRADE MEMBER
bellman Posted August 9, 2005 Posted August 9, 2005 great minds think alike bellman You win on typing speed though 64007[/snapback] Great but slightly addled mind Been drinking Guinness all day B) I'm on holiday believe it or not, brought laptop and mobile GPRS connection with me though, how sad is that As for the typing, i'm suprised I got there first, especially with my curent level of intoxication Regards Bellman Service Engineer and all round nice bloke ) The views above are mine and NOT those of my employer.
Mavrick_001 Posted August 9, 2005 Posted August 9, 2005 Your deff on too much dolla.... taht must be costing a fortune.... any bugger off and have a good holiday!!!!! CCTV Intruder Access Control Tony Hughes, Proprietor, TRADE MEMBER
bellman Posted August 9, 2005 Posted August 9, 2005 I wish mate, poor service engineer me. anyway, it's inclusive GPRS megabytes i'm using up, as usual with phone providers it's use it or loose it. I must really try to get out more Regards Bellman Service Engineer and all round nice bloke ) The views above are mine and NOT those of my employer.
Guest Posted August 10, 2005 Posted August 10, 2005 ...I must really try to get out more Regards Bellman 64022[/snapback] A........, T....., P....., etc..
Guest roonster Posted August 10, 2005 Posted August 10, 2005 Thanks guys, So i needs these then: http://actmeters.co.uk/actmeters.htm ACT1313 1414 Spike Suppressors How many should i order, one for each cable?