Recommended Posts

Guest aileinomuireasain
Posted

Can anyone advise me how to wire these into the control panel?

I can e-mail the instruction guides for the detectors or the panel itself, which is a Premier 24.

While the likes of the Pyronix ME 12 PIRs take 4K7 resistors, these ones don't seem to...and their instuctions don't say you use any resistors (but my panel's instruction guide says to use them in the zones as EOL (End Of Line) resistors).

As this is the DIY forum, please help me in very basic terminology i.e. white wire to +ve, green to -ve etc.

Alan

Posted

wire them as per the instructions in the install manual for the premier. :yes:

You only need to connect 4 wires between the panel and the detector 2 for power and 2 for zone, which colours you use to do this is irrespective. Although I'd suggest you use the same colours as the manual dictates so as to stop any possible confusion :)

Hope this helps

Regards

Bellman

Service Engineer and all round nice bloke :-)

The views above are mine and NOT those of my employer.

  • 4 weeks later...
Posted

normally you could wire the detector normally closed

red=12v

black=ve-

yellow=alarm

blue=alarm

green=tamper

white=tamper

their are other ways to wire these but this is about the most basic way.

Posted

The 24 can be wired double pole(2 alarm 2 tamper) or 2wire double end of line(2 resistors, 4k7 &2k2)

The opinions I express are mine and are usually correct!

(Except when I'm wrong)(which I'm not)