Hi guy's i put 2 Dual tec sensors in a conservatory and garage,

i put the wires as follows:

C | N/C | + | - | T2 | T1

B G R B Y W < Colours

to Panel as follows:

ZONE2 | + | - | TAMPER RETURN:

B G R B Y/W

everytime i walk test the system, it triggers the alarm and says 1012 +TAMP S/C

And sometimes it says 1012 +TAMP O/C

any idea's or help?

Regards,

J

Posted

You have not wired the EOL resistors correctly.

Sounds as though you have fitted both resistors in each detector. Each device does not require the 2x1K resistors when wired on just one zone you only need 3x1K resistors (1X Tamper & 1X accross each Zone).

****?**** ZONE2 | + | - | TAMPER RETURN.???? After properly reading your post, I have to wonder what you think your doing.?

Galaxy panels only require 4 wires per detector, Zone | + | - , and are wired EOL using 1K resistors.

........................................................

Dave Partridge (Romec Service Engineer)

Posted

Hey cheers for that,

i put 3x1k's from T2 to NC from NC to C and it come up with same problem?

i've never had it before i have no idea what it could be,

Regards,

J

Posted

Am I correct in assuming that you are trying to get both the conservatory and garage DT's both wired to the panel as 1 zone.?

........................................................

Dave Partridge (Romec Service Engineer)

Posted

No, i moved door contacts to zone 1001 front and back door on same

Moved zone 2 to Zone 1002 and put con and garage to zone 1011 and 1012

but it comes up with

1001 to 1012 +TAMP S/C

Regards,

J

Posted

Any help then guy's?

still cant solve it.

Regards,

J

Posted

Okay i put:

ZONE | + | -

And a 1K from T2 To NC from NC to C

now it shows up as

1011 +TAMP O/C

? :!:

Posted

JMancs,

have a look above at Dave's first reply. With EOL, you will only need to be using 4 wires from the detector to the panel, namely, power and EOL.

As I read it from your setup.

C to Zone

T1 to Zone

+ to +

- to -

Your PIR sounds like it is setup as follows

C to N/C through 1k

N/C to T2 through 1k

If you have a multi-meter, the pair should be at 1kR when idle, and 2kR when triggered.

Andrew

Any statement made or information provided in this post are the mere opinions of the author, and no inferrence is to be made as to the quality of information nor should any reliance be placed upon its contents.

Posted

Hey, i did a reading on the zones, it does a reading, from 900 upto 1230 which is good i'd say but everytime there is movement it triggers and says "Alarm in progress"

then when i put engineers codes in it comes up with 1012 +TAMP S/C or O/C

on idle it comes up with -0 on readings?

Posted

Ok, how is the zone programmed is it for 1k+1k EOL?

Is it definately wired like this:

C ------- Zone on panel (RIO)

|

1kR

|

N/C

|

1kR

|

T2

|

T1 ------ Zone on panel (RIO)

?

If this is the case, I don't see how a short could occur. An open circuit could however, occur if the EOL resistors or wires were lose. The variation in resistance you showed, was that just whilst the zone was secure?

Are the resistors both 1kR? (Black-Brown-Red + tolerance) or (Brown-Black-Black-Brown + tolerance)

Andrew

Any statement made or information provided in this post are the mere opinions of the author, and no inferrence is to be made as to the quality of information nor should any reliance be placed upon its contents.

Archived

This topic is now archived and is closed to further replies.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.